September 8th, 2004, 09:21 AM
#1
HB Forum Owner
As I understand 10-606 and 10-614, the bonding bushing and bonding jumper is only required where a metal service conduit enters the service equipment.
There is a sketch in the Code Handbook that illustrates this.
I believe that the original intent was to supplement the bonding afforded by concentric knockouts in the enclosure.
Ed
-
September 8th, 2004, 03:04 PM
#2
Inactive Member
An unfused service conduit would only need a ground busing on one end right? What if it has an emt coupling in it?
-
September 8th, 2004, 10:02 PM
#3
Inactive Member
On one end - right, even if it has a coupling.
A bond bushing is also required on the supply side conduit, if it enters the meter or splitter through a knock-out.